fluorescent fixtures, ballasts and safe circuit capacity

ezgrower(z5 IL)June 27, 2006

A simple (I hope) question arising out of my limited knowledge of ballasts in fluorescent light fixtures . . .

In determining the load that a fluorescent fixture contributes on a circuit, does the ballast figure in? That is, the load from 36 40W bulbs would just meet the safe "constant use" (80%) threshhold on a 15A circuit, but what about the ballasts in the fixtures? If ballasts make a contribution, where is the information to calculate it?

Thank you for reporting this comment. Undo
zink(6a)

ez,

Here is the extra power consumed by the ballasts. These figures are per each bulb:

Magnetic Ballast(40w) = 6.0 watts
Electronic Ballast Rapid Start (32w) = 3.5 watts
Electronic Ballast Instant Start (32w) = 2.5 watts

Zink

    Bookmark   June 28, 2006 at 10:57AM
Thank you for reporting this comment. Undo
jagermeister

Also, the amps that the ballast draws is always printed on the ballast case. In the case of the HD Sunpark ballasts, it's 1.0 amp. And that's probably a maximum figure at startup.

    Bookmark   July 12, 2006 at 9:08AM
Sign Up to comment
More Discussions
New to Forum - some questions, comments about heating mats
I have been starting flower seeds indoors for years...
snapdrag
Cost-Efficient Lighting
Does anyone know what the most cost-efficient lighting...
Tigger033
More beautiful plumeria blossoms under grow lights
More proof that grow lights work! I planted this plumeria...
arctictropical
HELP!..Possible Indoor Pepper growing probz!
I have a few questions regarding my pepper plants at...
Bobby Cooper
Correcting Lighting Later?
Hello, I am germinating Palmer amaranth for an experiment...
Tigger033
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™